So the master switch in my consumer unit which trips out if there's a short anywhere in the house is actually an RCBO and not (as I tend to refer to it) an RCD?
MCB - Miniature Circuit Breaker - Trips on over current. Its rating will be marked on it and it is guaranteed not to trip when that amount of current is going through it. Its actual trip current will be quite a bit higher. No test button.Penners said:So the master switch in my consumer unit which trips out if there's a short anywhere in the house is actually an RCBO and not (as I tend to refer to it) an RCD?
To put what MdB said in a nutshell, no.Penners said:So the master switch in my consumer unit which trips out if there's a short anywhere in the house is actually an RCBO and not (as I tend to refer to it) an RCD?
Rather than a short.Lime said:To put what MdB said in a nutshell, no.Penners said:So the master switch in my consumer unit which trips out if there's a short anywhere in the house is actually an RCBO and not (as I tend to refer to it) an RCD?
Almost certainly the switch you describe is an RCD.
It trips out because there is a leakage to earth.
I don't think that's strictly correct, at least not in a 'wiring regs' sense.MdB said:If you don't have your own 80A MCB then you need to have one.
Indeed, although a short may occur at the same time.MdB said:Rather than a short.Lime said:To put what MdB said in a nutshell, no.Penners said:So the master switch in my consumer unit which trips out if there's a short anywhere in the house is actually an RCBO and not (as I tend to refer to it) an RCD?
Almost certainly the switch you describe is an RCD.
It trips out because there is a leakage to earth.
Agreed.MdB said:If it has a test switch then it is an RCCB (RCD) or an RCBO (unlikely for the whole house).
Penners said:the occasional nuisance trip of an MCB or the RCD - principally when a light bulb blows
Penners said:I understand the basic principles that have been explained but I'm a little hazier on some of the subtleties. However, bottom line, it sounds as though our installation, with a correctly rated MCB on each circuit and an RCD (I think) protecting the whole CU, is an acceptably safe configuration.
It would be interesting to know if the RCD ever trips when a light bulb blows. I can imagine a blowing bulb causing a momentary over-current surge causing an MCB to trip but I can't imagine one causing an RCD to trip because they only have the live & neutral conductors within the glass so any current cannot 'leak' away to cause the required imbalance to trip an RCD. Unless they can be susceptible to a current surge?Penners said:Yes, we do get the occasional nuisance trip of an MCB or the RCD - principally when a light bulb blows - but I can live with that.
MdB said:Having one RCD for the whole house isn't recommended now and wouldn't (??) be done for a new installation. 16th addition (I think) recommends splitting the house in two with to RCDs so that half of the lights are on the one RCD and half on the other. This way when one trips, there is still lighting in the building somewhere. 17th addition (I think) takes this further and suggests using RCBOs so that you lose on a single circuit when a trip occurs. It is certainly sensible to have the freezer on a different RCD / RCBO to everything else.
The above might not be absolutely correct in the details but you get the idea.
Flyfisher said:I wonder how long it will be before RCBOs on every circuit becomes standard?
They are around £15 each if you shop around so not too bad. I think one for the freezer by itself is essential. I also have one for the landing light and the mains powered smoke alarms. This way if the rest of the house trips there is still light available to most of the rest of the house and the smoke alarm is still active. If it trips itself, the landing light won't work which will warn me that the smoke alarms are out. The rest I guess are less essential but nice if you can spare the few £ extra.FamilyWiggs said:Bit of unecessary expense isn't it?
A single RCD protrotecting all the circuits and detecting earth leakage, with individual MCBs protecting each circuit from overcurrent seems adequate.
FamilyWiggs said:Bit of unecessary expense isn't it?
A single RCD protrotecting all the circuits and detecting earth leakage, with individual MCBs protecting each circuit from overcurrent seems adequate.
Thanks for the reassurance, FF.Flyfisher said:It would be interesting to know if the RCD ever trips when a light bulb blows. I can imagine a blowing bulb causing a momentary over-current surge causing an MCB to trip but I can't imagine one causing an RCD to trip because they only have the live & neutral conductors within the glass so any current cannot 'leak' away to cause the required imbalance to trip an RCD. Unless they can be susceptible to a current surge?