Be very very careful about this. The amount of current a cable can take is independant of its length. A short length of cable with 10A going through it will get just as hot as a long length of the same cable with 10A going through it.AMc said:I suspect that the thinner cable can be used because the length of cables are precut and the ease of installation is balanced against the loss in efficiency in heat from the cable. A 12v loop of the same length as a standard lighting circuit would be a terrible idea.
Just to make this clear, a little 35W, 12V bulb requires 3A to flow through its cable where as a 100W, 240V bulb requires only 0.42A. This is a factor 7 difference and hence the low voltage bulb needs a cable 7 times thicker for a fraction of the light output.
In my previous house, I had a string of five 12V 35W halogen bulbs which I wanted to switch on and off at the low voltage side. This meant I could not use a standard lighting switch as these are only typically rated as 10A. After a long search, I found a suitable 20A switch which was capable of dealing with the 15A load. (If I has switched these lights at the 240V input, the current would have been only 0.7A so any old mains rated switch would have been fine)