I'm still not convinced, you really need to do some tests. I would do the following and let us know the results.Jon Maine said:1/ Incoming pressure fine.
2/ Pump and nrvs exactly the same on both circuits so no problem there
3/ Probably the problem
a) Starting pressure reading (4.5 bar?)
b) Open hot tap - measure pressure whilst hot tap is open (1 to 2 bar?)
c) Close hot tap - measure pressure (3 bar?)
d) Leave system for 5 mins whilst not using any water at all - measure pressure (?)
e) Leave system for a couple of hours whilst not using any water at all - measure pressure (?)
If you do the above then we should be able to rule in or rule out some of the possible causes.