Not really a period property topic, although it could help avoid disrupting existing fabric when running a new cable and I know there are some qualified electricians lurking here.
A friend (yes, really!) has a built-in microwave oven that has just failed. Should be a simple enough job to replace it, I thought.
The failed microwave had a standard 3-pin plug and the cupboard above has a standard socket on the kitchen ring-main. Unfortunately, the replacement microwave cable is not fitted with a 3-pin plug as it requires a 16A supply. It seems that microwaves have moved on over the past 20 years or so and while there are plenty of standalone microwave-only models, all the models designed to be built-in are combination microwave ovens and this particular Bosch model is rated at 3350W, hence the 16A requirement, hence the lack of a standard 13A 3-pin socket
So to my question: can a switched, fused spur with flex outlet be connected to the existing ring-main socket and the microwave connected to the fused spur?
My thinking is as follows:
1. The failed microwave has been connected to the ring-main circuit for about 20 years without any problems, albeit via a 13A 3-pin plug/socket
2. The kitchen already has a separate double oven plus an Aga so the chances of the new microwave being used as an oven is very remote and the microwave-only function is only rated at 900W, so well within the 13A fuse in the switched spur
3. Even if the microwave is used as an oven, the 3350W (14A) rating is well within the rating of the switched spur and associated cabling and only slightly over the 13A fuse rating, so the fuse would take a fair while to blow.
4. Even if the fuse does blow, it would only be a nuisance and wouldn't be an electrical safety issue.
Based on this, I'm fairly sure that a switched fused spur off the existing ring main would be electrically safe, so my real question is would it comply with the latest wiring reg and would a qualified electrician install and certify this solution?
I'm guessing that the only alternative would be to run a new dedicated circuit back to the consumer unit and use a 16A RCBO but it won't be an easy job to run a new cable without significant disruption to the kitchen and walls, hence my question.
Any thoughts?
A friend (yes, really!) has a built-in microwave oven that has just failed. Should be a simple enough job to replace it, I thought.
The failed microwave had a standard 3-pin plug and the cupboard above has a standard socket on the kitchen ring-main. Unfortunately, the replacement microwave cable is not fitted with a 3-pin plug as it requires a 16A supply. It seems that microwaves have moved on over the past 20 years or so and while there are plenty of standalone microwave-only models, all the models designed to be built-in are combination microwave ovens and this particular Bosch model is rated at 3350W, hence the 16A requirement, hence the lack of a standard 13A 3-pin socket
So to my question: can a switched, fused spur with flex outlet be connected to the existing ring-main socket and the microwave connected to the fused spur?
My thinking is as follows:
1. The failed microwave has been connected to the ring-main circuit for about 20 years without any problems, albeit via a 13A 3-pin plug/socket
2. The kitchen already has a separate double oven plus an Aga so the chances of the new microwave being used as an oven is very remote and the microwave-only function is only rated at 900W, so well within the 13A fuse in the switched spur
3. Even if the microwave is used as an oven, the 3350W (14A) rating is well within the rating of the switched spur and associated cabling and only slightly over the 13A fuse rating, so the fuse would take a fair while to blow.
4. Even if the fuse does blow, it would only be a nuisance and wouldn't be an electrical safety issue.
Based on this, I'm fairly sure that a switched fused spur off the existing ring main would be electrically safe, so my real question is would it comply with the latest wiring reg and would a qualified electrician install and certify this solution?
I'm guessing that the only alternative would be to run a new dedicated circuit back to the consumer unit and use a 16A RCBO but it won't be an easy job to run a new cable without significant disruption to the kitchen and walls, hence my question.
Any thoughts?