. . . or more accurately, modern electrical regs in period houses.
Like many period properties we have rooms with just one doulbe socket and even some without any at all. In some of these rooms the double socket has been spurred off a ring main, which I understand is perfectly ok (unless I'm out of date with the latest regulations).
I would like to add some more sockets to various rooms but my understanding is that only a single spur is allowed off a 30A ring main, which makes sense.
My question is whether it is acceptable to replace the 30A MCB for the ring main with 20A (or even 16A) and then add more than one spur, effectively creating a radial circuit? Thus, the 20/16A MCB would correctly protect both the 2.5mm2 radial cabling and the existing 2.5mm2 ring cabling. I'm confident such a thing is electrically ok in terms of cable ratings and fuse protection but I'm less sure about the more 'esoteric' regulations such as diversity in 'living' rooms (ie not a kitchen) and sockets-per-floor-area guidelines etc.
I appreciate that the total power capability of the circuit will be dramatically reduced but for the typical modern mix of TV, hi-fi system, chargers for phones/tablets/laptops and table or standard lamps even 16A will be perfectly fine. And in the unlikely event that someone plugs in two 3kW fan heaters then the MCB will trip to protect everything from overloading (just as a 30A MCB would trip if someone plugged three such fan heaters into the same ring main).
Like many period properties we have rooms with just one doulbe socket and even some without any at all. In some of these rooms the double socket has been spurred off a ring main, which I understand is perfectly ok (unless I'm out of date with the latest regulations).
I would like to add some more sockets to various rooms but my understanding is that only a single spur is allowed off a 30A ring main, which makes sense.
My question is whether it is acceptable to replace the 30A MCB for the ring main with 20A (or even 16A) and then add more than one spur, effectively creating a radial circuit? Thus, the 20/16A MCB would correctly protect both the 2.5mm2 radial cabling and the existing 2.5mm2 ring cabling. I'm confident such a thing is electrically ok in terms of cable ratings and fuse protection but I'm less sure about the more 'esoteric' regulations such as diversity in 'living' rooms (ie not a kitchen) and sockets-per-floor-area guidelines etc.
I appreciate that the total power capability of the circuit will be dramatically reduced but for the typical modern mix of TV, hi-fi system, chargers for phones/tablets/laptops and table or standard lamps even 16A will be perfectly fine. And in the unlikely event that someone plugs in two 3kW fan heaters then the MCB will trip to protect everything from overloading (just as a 30A MCB would trip if someone plugged three such fan heaters into the same ring main).