Our new electric range cooker arrives next Wednesday, so I've been trying to check that the existing cabling and fusing is sufficient to support the load. Anyone got any comments on the following, please (e.g Zebra, FF, etc.)? :-
Total power consumption of all the cooker's heating elements: 13.8kW
I believe the diversity factor for cookers suggests a load calculation of 10A plus 30% of the remaining total load.
I calculate the total load as 13800/240 = 57.5A
57.5 - 10 = 47.5
47.5/3 = 15.8 + 10 = 25.8A nominal load
Based on that I'm assuming that a 40A minibreaker in the consumer unit and 6mm^2 supply cable will be a proper spec. I'd be very grateful for any comments to agree or disagree with that, please!